Sistering Joist Issue

Hi all,

I am currently remodleing my batroom an planning on laying ceramic tile.

I have 2x6 redwood joist, 16 inch on center spacing and 10ft between beams.

with what looks like 1/2 oak subfloor, using 1/2 ply OSB and 1/4 hardibacker.

I know this does not meet the proper delflection for tile, so I sitered up the joist.

Clearly I did not do enough research as I sister up the joist with 2x4s with 12inch spacing.

I now know I should have been using 2x6, but do you think the 2x4 at 12inch spacing will be enough to meet the 360 deflection I need.

Has anyone else done this?? what are the results, or do i need to get under the crawl space again?

Thanks

Alan
__________________
Alan
Alan D is offline   Reply With Quote
Sponsored Links
Unread 08-12-2009, 12:11 PM   #2
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 96,779
Welcome, Alan.

Not sure just how a fella would sister 16"oc joists with sisters 12"oc. You're gonna hafta help me with that one.

Perhaps you could post us a picher of what you've done? We like pichers.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 08-12-2009, 12:25 PM   #3
Alan D
Registered User
 
Join Date: Aug 2009
Posts: 9
The 2x4 that is sistered in between 16oc joist fit all the way, approximatley 14.5 inches in length.

and I spaced them 1ft apart along the joist

SO for a section of joist that run 11ft in the bathroom, I put in 11 sistering
2X4's.

Does it make sense yet?

Sorry new to this stuff
__________________
Alan
Alan D is offline   Reply With Quote
Unread 08-12-2009, 12:36 PM   #4
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 96,779
Well, yeah, kinda, 'cept that's not sistering, Alan.

And, unfortunately, that's done you no good at all.

What you've done is install partial blocking between your joists. While that could have some effect upon the between-joist deflection of your subflooring, it has no effect whatever on your woefully overspanned joists.

What you need to do is remove that blocking (I know, I know) and actually sister those joists by adding an additional joist of equal or larger size beside the existing joists. If you use 2x6 material for your sisters, you'll really want to select a more suitable wood specie, also. Southern Yellow Pine and Douglas Fir are a couple common species of framing lumber that are generally available in most areas.

The alternative is to provide a mid-span support beam or wall under the existing joists to reduce the unsupported span. Can't tell if that's an option for you or not.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 08-12-2009, 12:53 PM   #5
HammerMill88
Registered User
 
Join Date: May 2009
Location: Artesia, MS
Posts: 138
CX's 2nd option is the one I would go with since u have already installed blocking.

Just double u up a 2x6 beam 1/2 way that spans across all joists. Use some 2x12 double-joist hangers (at least4 to keep beam from rolling) to support beam where it touches the lowest joists. Those it does not contact, cut some "just tight" shims.

Support ends of beam with concrete blocks or floor-jacks (more expensive). Just tighten unless u want to get any sag out of ther floor at this time.

That's what I would do.

Good luck!
__________________
Joey

"Necessity is the plea for every infringement of human liberty; it is the argument of tyrants; it is the creed of slaves." William Pitt
HammerMill88 is offline   Reply With Quote
Unread 08-12-2009, 01:05 PM   #6
Alan D
Registered User
 
Join Date: Aug 2009
Posts: 9
Thanks for the info guys,

I had this all incorrect to start with. I was thinking of deflection of the boards between joist, not the actual deflection of the joist between the beam.

Looking back at it, the 5 or 6 of the joist joist that span the width of the bathroom about 3 of those had already been sistered (the real Sistering)
and I recall seeing 2 cinder blocks underneath one of the sections.

I will need to go look at it all again, but now I understand what is meant to be happening.

So hopefully I just have to sister up the remaining 3 joist.

Thanks again
__________________
Alan
Alan D is offline   Reply With Quote
Unread 08-12-2009, 01:17 PM   #7
Alan D
Registered User
 
Join Date: Aug 2009
Posts: 9
Actually,

Was just thinking about joey's thread and it seems a pretty good option too and may take that course of action.

Just a question about doubling up the 2X6

Do I double up so it ends up being a 2X12 of a 4x6

Possibly a dumb question seeing as you said a 2 X12 joist hanger but it just seems a little odd to me, but what would I know considering my previous efforts. haha

Thanks
__________________
Alan
Alan D is offline   Reply With Quote
Unread 08-12-2009, 01:40 PM   #8
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 96,779
You'd customarily "sister" the joists to create a 4x6 using two 2x6s, Alan. If you could find a way to actually attach the members such that you end up with a 2x12, that would be far, far more rigid, but I don't have any eye dee how a fella'd do that.

I also have no eye-dee what Joey had in mind for his 2x12 joist hangers, either. Maybe he'll tell us.

For adding the mid-span support, his suggestion of doubled 2x6s would be OK so long as you have a way to support the new beam every five or six feet. It's usually easier to use deeper beams and fewer supports, but I can't see what's under your floor from here.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 08-12-2009, 01:53 PM   #9
Edthedawg
Wannabe Engineer Old-house-nik DIY'er :)
 
Edthedawg's Avatar
 
Join Date: Jun 2009
Location: NE CT
Posts: 2,062
the 2x12 joist hangers are a good idea to hang/hold it all together while working by yourself in a situation like this. Hang 'em on one end of the existing 2x6's so that about 5 3/4" hangs down - enough to easily slide in a new 2x6 that will run across below all the existing 2x6 joists. Then get the new piece in, lift the far end up, and attach it tight w/ another 2x12 joist hanger on that end.

I might look for a 4x12 so i could put up a sistered pair of 2x6's running across the span. Less apt to tip/rock, plus better strength as a pair.

Or if this is getting ANY exterior exposure (I think the word crawlspace was used, dunno if that's interior or outside) one might contemplate using a PT 4x6 to do this work.
__________________
Ed

GO SOX!

Pleased to have helped design and build many of the residential projects featured here: http://www.tandtdev.com/portfolio.html
Edthedawg is offline   Reply With Quote
Unread 08-12-2009, 05:28 PM   #10
HammerMill88
Registered User
 
Join Date: May 2009
Location: Artesia, MS
Posts: 138
Yeah Alan, sorry about the informality earlier...Welcome aboard! There are some really good, knowledgeable people here.

Ed kinda hit on the 2x12 joist hangers. The 2x12 gives you enough hanger to nail onto the joists. You have 5 1/2" of doubled beam on the bottom part of hanger, and the top 5" of the hanger nails into the joist.

At the minimum, I would have a hanger every 48" (e.g. 16" o.c. = every third joist & 24" o.c. = every other joist). Use the 10d 1 1/2" approved hanger nails. They have the shear strength necessary for this application.

I like using 2x stock b/c of opposing grains can make stronger and less twisting than 4x stuff. Down here in MS, we use PT pine stuff as much as possible. If using PT, make sure you use PT approved fasteners and nail/screw the piss out of them together (more is better!).

CX is right. I said put supports at ends. He is more correct that you don't want more than say 6' span b/w pillars for the 2x6's. I would figure about 5 1/2' per support. That means you can have about 2 1/2' hang-over on the ends. I wouldn't really want to go a full 3'. So, for 2 pillars, you could max out at 11'. If you want to push 12' do at your own discretion, but you are better widening on the inside than more hang-over (IMO).

Remember, when "shimming" use "opposing wedges," and just tighten b/w any high joists and then beam. Don't over do it. If using PT, you may want to come back every other week for 6 weeks or so b/c most PT is still wet and will shrink when drying out. You may even have to shim where the beam once touched the joist.

Again, good luck. Also, there are no "stupid" questions, only uninformed/misinformed.

Don't hesitate to ask for further assistance. These guys rock!
__________________
Joey

"Necessity is the plea for every infringement of human liberty; it is the argument of tyrants; it is the creed of slaves." William Pitt
HammerMill88 is offline   Reply With Quote
Unread 08-12-2009, 05:34 PM   #11
HammerMill88
Registered User
 
Join Date: May 2009
Location: Artesia, MS
Posts: 138
Edit: Nailing 2x's together.

Remember, crown, if any goes up. Pick through and find two good pieces with a very slight crown.

Also, if you have a good table saw. Once you nail them together (watch out for nails sticking through), run them through the table saw to trim the edges even to again aid in support and prevent rolling.

If not table saw. Lay them on top of one another and scribe the one that is larger, then trim with skil-saw. You may have to trim both pieces. IMO, this is an imperative step. Top and bottom need to be flush and flat, within 1/32 at least.
__________________
Joey

"Necessity is the plea for every infringement of human liberty; it is the argument of tyrants; it is the creed of slaves." William Pitt
HammerMill88 is offline   Reply With Quote
Unread 08-14-2009, 12:05 PM   #12
Alan D
Registered User
 
Join Date: Aug 2009
Posts: 9
About to lay Hardibacker on Subfloor w/ mortar

Hi again,

I am about to lay down my hardibacker onto the subfloor with mortar, and I was wondering how long till I can walk on it and set my bath tub on top of it.

Obviously I will need to screw it in after it is set down so It will have some pressure applied to it, but will it be ok to walk on or set the bath in.

Or do I need to wait 24hrs

and for the guys who helped me out before, Just want to let you know that I installed the extra 2x6 joist halfway along my bath room so the spacing is more like 5 feet insted of 10feet. Used cinder blocks and wood to hold it up, I just need to fill in a few gaps between the new joist and original joist, and keep an eye on it over the next couple of months.

Thanks again
__________________
Alan
Alan D is offline   Reply With Quote
Unread 08-14-2009, 12:11 PM   #13
Rd Tile
Tile Man
 
Join Date: Nov 2003
Location: Long Island N.Y.
Posts: 6,892
Is this a free standing tub?

Tubs should be installed over the plywood or subfloor first, then CBU up to it, guess it could be done either way.

But you can set the tub any time after if you like.
__________________
Richie.
Rd Tile is offline   Reply With Quote
Unread 08-14-2009, 12:17 PM   #14
Alan D
Registered User
 
Join Date: Aug 2009
Posts: 9
not too sure what you mean by free standing tub?

Does that that mean it is not held in by screws etc???

It is a old, heavy as hell tub, the side of the tub towards the wall sits/rest on a piece of wood that runs the length of it, and the side that you step in from goes down to the ground, so it has its own wall, if that makes any sense.
__________________
Alan
Alan D is offline   Reply With Quote
Unread 08-14-2009, 12:19 PM   #15
Rd Tile
Tile Man
 
Join Date: Nov 2003
Location: Long Island N.Y.
Posts: 6,892
OK, I always install the tub you have first, then build the subfloor for the tile up to it.


Free standing tub.
http://www.signaturehardware.com/editor/tubguide.html
__________________
Richie.
Rd Tile is offline   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Ready to lay hardibacker. Subfloor squeeking??? kayakers2 Tile Forum/Advice Board 4 06-05-2008 08:33 AM
Can I lay subfloor over boards? Donnie740 Tile Forum/Advice Board 1 12-31-2005 07:41 AM
how to lay subfloor over existing tile Unregistered Tile Forum/Advice Board 2 06-30-2004 07:01 AM
plumbers by and large lay vinyl directly on subfloor Kaydee Tile Forum/Advice Board 7 10-13-2003 06:11 AM
Mortar for under Hardibacker John Tile Forum/Advice Board 3 06-07-2002 01:57 PM


All times are GMT -6. The time now is 07:00 AM.


Sponsors

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2023, Jelsoft Enterprises Ltd.
Copyright 2018 John Bridge & Associates, LLC