Air Tight steam shower advise

Hello All. I have been slowly buliding a steam shower enclosure for the past couple years. I am a first timer. To date, here is what I have accomplished, but need to confirm my next steps.

The walls:
1 - Shower is located in corner of home so we have two exterior walls.
2 - traditional framing - insulated, plastic vapor barrier then:
3 - green board which is then sealed over with waterproof membrane then:
4 - 1/2" cement board.

Mud pan is in with preslope. I tested prior to putting in the sand mix and all is water tight. Pan does weep water to the drain as its supposed to.

Questions I need to ask:

I have two IC recessed cans in the ceiling. I think I took bad advise from lighting contractor. I am not comfortable with the ability of these fixtures to be air tight. My gut tells me to remove them and put in flush mount, wet location type fixtures. YES/NO?????

Do I need to put a waterproofing membrane on the cement board prior to tiling???

What do I use to seal and make the shower heads, thermo comtrol, and shut offs airtight behind the tile??? Silicone???

Any advise is greatly appreciated

Regards, Joe
steiner689 is offline   Reply With Quote
Sponsored Links
Unread 02-26-2008, 09:07 AM   #2
nforcer2
Registered User
 
Join Date: May 2006
Posts: 494
Your first issue is the use of greenboard. Regardless of the fact there is a roll on membrane on the surface, forced vapor emissions will transmit through that membrane. You need to have a cement backer board such as Durock, Permabase or wonderboard as your substrate. The greenboard needs to be removed. Is most states it is now approved for use in wet areas and certainly is not for use in an area exposed to constant moisture such as a steam shower. The use of an additional membrane over the walls is one that is seen here as taboo by most due to the creation of a possible "moisture sandwich". That is debatable. =)
__________________
Robert Goff
LATICRETE Tech Rep
www.laticrete.com
nforcer2 is offline   Reply With Quote
Unread 02-26-2008, 09:10 AM   #3
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 89,553
Welcome, Joe.

I sure wouldn't be worrying about those ceiling lights when I had sheetrock sandwiched in my walls.

I hate to be a wet blanket, but that's just not gonna work out well.
Quote:
Do I need to put a waterproofing membrane on the cement board prior to tiling???
You would normally want a vaporproof membrane over that CBU, including the ceiling.

There are some vaporproof trims that can be had for some recessed lighting fixtures.

Silicone or Urethane caulking can be used around your plumbing penetrations.

But ain't none of that gonna save your sheetrock. What was the thinking behind that part of the installation?

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 02-26-2008, 09:42 AM   #4
steiner689
Registered User
 
Join Date: Apr 2005
Location: cincinnati
Posts: 18
Send a message via AIM to steiner689
Thank for the input. Just to clarify. The "membrane" over the green board is not a roll-on vapor barrier but a rubberized peal and stick exterior roofing membrane. Totally waterproof. It is about 20 mil. The logic was to use the green board and the roofing membrane to protect to exterior wall insulation. A traditional piece of 6 mil plastic stapled to the studs did not seem to be enough to protect vapor form penetrating to the insulation. I do understand the taboo of not using an additional membrane on the cement board to avoid creating a sandwich. But, isn't a sandwich created with traditional 6 mil plastic-cement board-then roll on membrane?? When I installed the Choroloy, I overlapped the roofing membrane to cover the top edge of the Choroloy sticking it to the greenboard. The entire shower enclosure is covered with the roofing membrane. Filled the pan with water above that line to test it and had no wicking or seeping of water into the green board. Overkill or do I have a do over?????

Thanks Again.

Joe
steiner689 is offline   Reply With Quote
Unread 02-26-2008, 10:33 AM   #5
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 89,553
Don't know if your roofing membrane material is a vapor barrier or not, Joe. At 20 mils thickness it certainly could be.

But then you've penetrated it with the fasteners for the installation of your CBU, have you not? And then behind the sheetrock you've installed another vapor barrier material (6mil poly), but it's also penetrated by all the fasteners for the sheetrock and the CBU.

So you've got a pretty effective moisture sandwich with sheetrock inna middle. Vapor from the steam shower will have a great deal of incentive to enter that sandwich area, and not much incentive at all to exit. By and by (think a few years of use) there will be moisture in there with the sheetrock that has no effective way to escape. This is never a good thing.

How long until you see a problem? Can't say. But I'm willing to bet large that you'll have wet sheetrock in the lower portions of that wall in a year or so of regular use.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 02-26-2008, 11:04 AM   #6
steiner689
Registered User
 
Join Date: Apr 2005
Location: cincinnati
Posts: 18
Send a message via AIM to steiner689
The rubberized roofing membrane self seals when a fastner is driven/screwed through it. I am not concerned about vapor getting through the screw holes of the roofing membrane . But what you are saying is that I have would a double decker moisture sandwich with the plastic - greenboard - roofing membrane - CBU - then roll on vapor barrier such as Lactite. The entire objective of this sequence was to prevent moisture from getting into the exterior wall cavity.
steiner689 is offline   Reply With Quote
Unread 02-26-2008, 11:08 AM   #7
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 89,553
You may have accomplished that. Still think you have a problem, though.

Did you do the ceiling the same way?
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 02-26-2008, 11:18 AM   #8
steiner689
Registered User
 
Join Date: Apr 2005
Location: cincinnati
Posts: 18
Send a message via AIM to steiner689
Yes. Ceiling is same, which is the second floor. Blown in insulation above. Per your other post, what prevents moisture from getting into the wall cavity when a plastic vapor barrier is the only thing that used behind the CBU. Aren't the screw/nail holes always created regardless of what is used when the CBU is attached?? What is the recoomended Vapor barrier to use behind the CBU on exterior walls???Should I have used styrofoam insulation instead of batts??? Thanks for all of the input. If I remove the Steam Component, do you feel I will still have a problem, but just prolonged longer??? You've really have me thinking....

Thanks Again, Joe
steiner689 is offline   Reply With Quote
Unread 02-26-2008, 11:30 AM   #9
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 89,553
The vapor barrier comes into play only for steam showers, Joe. For regular showers the poly behind the CBU is a moisture barrier.

The intent is still to keep moisture out of the wall cavity, but the vapor pressure in a regular shower is not as high as in a steam shower and the poly or roofing felt is generally considered sufficient.

If yours were not a steam shower, your wall cavity would be well protected from moisture from the shower. Long term I think you'll still suffer from the poly and roofing membrane sandwiching the sheetrock. How long term? I dunno.

Some folks treat residential steam showers the same as regular showers because "they don't get used much." I don't like that approach. If there is a steam shower available, somebody could use it daily. Still not the same as the room at the local spa, but still enough to create the known problems.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 02-26-2008, 11:53 AM   #10
steiner689
Registered User
 
Join Date: Apr 2005
Location: cincinnati
Posts: 18
Send a message via AIM to steiner689
OK. To start over. I need to take down the CBU and then the green board covered with the roofing membrane. Wifey is going to love this one. I am now at 6 mil plastic covering insulation/studs. To rebuild, what is your recommended sequence. I may have to remove the shower pan in order to get the greenboard out that is behind it. May as well start form compete scratch. Thanks for all of your assistance.

Joe
steiner689 is offline   Reply With Quote
Unread 02-26-2008, 12:41 PM   #11
Scooter
Remodeler -- Southern Cal.
 
Scooter's Avatar
 
Join Date: Oct 2001
Location: Southern California
Posts: 4,345
Studs. 6 mil plastic. CBU. Steam Room approved membrane which is vapor proofed.
__________________
Scooter
"Sir, I May Be Drunk, But You're Crazy, and I'll Be Sober Tomorrow"
WC Fields, "Its a Gift" 1934
Scooter is offline   Reply With Quote
Unread 02-26-2008, 12:53 PM   #12
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 89,553
Not me saying it's gotta be torn out, Joe. I'm just trying to give you the theory as I see it. You wanna go with what you've got and see how it works, that's fine. Come back in a few years and educate the rest of us maybe.

I don't agree with Scooter's method, either. I think you should use a real vapor barrier membrane on the inside of the shower and nothing else.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 02-26-2008, 01:32 PM   #13
steiner689
Registered User
 
Join Date: Apr 2005
Location: cincinnati
Posts: 18
Send a message via AIM to steiner689
So, full circle. If I leave what I have with steam potential, would you waterproof the CBU before tiling. If I leave as is and remove the steam component/generator so the enclosure is regular shower would you waterproof the CBU before tiling. If I tear out and rebuild from scratch after the divorce... its all moot anyway. Thanks for all of the input. I guess it boils down to the preformance of the roofing membrane and if it can keep any moisture/wetness from penetrating into the green board.

-Joe
steiner689 is offline   Reply With Quote
Unread 02-26-2008, 02:51 PM   #14
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 89,553
If you have a lot of confidence in that membrane you used, I wouldn't do anything else to the inside of the shower. You'd just start getting into double-decker moisture sandwiches, eh?

If you wanna keep what you have, I'd just finish it up. If you wanna kill them two birds, tear it out and hope there's enough dinero left after the divorce to build it again.

But, hell, won't be your house then, anyway, eh?

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 02-26-2008, 03:02 PM   #15
Star
Pete
 
Join Date: Jun 2005
Location: Quebec, Canada
Posts: 238
Quote:
But, hell, won't be your house then, anyway, eh?


-pete
Star is offline   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -6. The time now is 01:20 PM.


Sponsors

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2020, Jelsoft Enterprises Ltd.
Copyright 2018 John Bridge & Associates, LLC