Schluter Mistakes - Fix or Fine?

Bathroom remodel with many mistakes by tile subcontractors-- GC willing to fix them--if I tell him which ones. In the interests of time (8 weeks now with no shower) and reasonability, I would be so grateful for your opinions on which mistakes you would let slide and which you would have fixed. All of the products are Schluter. Mistakes = not pursuant to Schluter installation instructions as I read them.

Bathroom floor - Schluter all-set, ditra heat
Shower (formerly closet) - Kerdi board, kerdi-line drain, ditra heat flooring

1) the ditra heat cable was run between the wall and bathtub, a 3" space. The cable will be under the outer edge of the bathtub, just barely

2) In the shower, the kerdi-board seams and all corners are covered with lots of Kerdi-fix, not kerdi-band

3) In the shower, the screws are also covered with kerdi-fix, not kerdi-band

4) shower floor layers - plywood, Schluter all-set, ditra heat, mapei ultraflor modified thin-set mortar (should I have them replace the mapei with the all-set)

5) ditra heat cable is not embedded in matting around the kerdi-line drain, it is placed on kerdi-membrane on the sides of the drain (the drain is at the entrance of the shower and not much room for the matting on the sides)

6) the kerdi-line drain channel is fit into a rectangle hole of the same size in the subfloor. it is connected to plumbing and just the edges of the channel are mortared to the sides of the subfloor. (GC wants to know how I want this to be fixed)

7) the shower floor is higher than the bathroom floor on the other side of the kerdi-line drain
__________________
Kate

Last edited by KKief; 06-20-2019 at 08:15 PM.
KKief is offline   Reply With Quote
Sponsored Links
Unread 06-21-2019, 07:19 AM   #2
speed51133
Registered User
 
Join Date: May 2017
Location: Milwaukee WI area
Posts: 1,223
With respect to the Kerdifix used as an all purpose goo:

Kerdifix is NOT approved to be used as waterproofing sealant. Think of it as a glue, that MAY seal water, but it also might leak.

It is used to adhere kerdiboard to things and adhere kerdi to things. The waterproofing is always supposed to be from overlapping kerdi membrane with an approved thinset as the bonding agent of the two membranes.

Will his method work? In my minimal experience, probably, BUT I have seen examples where water still wicks through in applications such as yours. You may be safe in a wall, as the examples of leaks I have seen were on the floor. Nevertheless, Schluter would call your installation erroneous and not warranty it, if you ever tried. While the GC may say HE will warranty it, you won't know if you have a small leak for months or even years, depending on the size, how often it is used, etc.

Not sure how to fix it without creating a big speed bump. We would have to see just how much kerdifix was used. Are you sure it was ACTUAL kerdifix? That stuff is expensive, would not surprise me if he used some other random sealant.

With respect to the questions on the linear drain and dirtra heat, I do not know. I have never used either.
__________________
Mike
speed51133 is offline   Reply With Quote
Unread 06-21-2019, 09:26 AM   #3
Elkski
Took the Schluter part 1 class my team won!
 
Elkski's Avatar
 
Join Date: Apr 2007
Location: Wasatch front, Utah
Posts: 848
#1 is it the actual heating portion of the cable? Or the unheated lead? The shaded portion is supposed to be 2 in away from cabinets I think they worry if it's in too much of a confined area it will overheat. What will be between the cable and the bathtub? did they run it in some kind of Groove to protect it or in ditra heat matting?
I don't think this is a big issue if it won't get crushed and isn't heating portion.
#2 they can just cover the seams with Kerdi band hopefully there's not a hump of Kerdi fix.
#3 I have not used the Kerdi board and screws but I thought covering with kerdi fix was ok
#4 are you saying they want to use ultra modified under your tile?
Or they have used it to fill the voids before tiling? Many people do use a modified between ditra and tile it does not meet the warranty unless it's all set or unmodified.
#5 I guess you're saying in order for the heating cable to get into the shower it has to go across the drain and the membrane is the only place that it can cross so that means ( the drain picked was to long) it will not be protected very much but as long as your thin set is 1/4" thick it should be okay as long as it's protected during the tiling process but you may want to call schluter about this.
#6 so you're saying the flange is just a thickness of thin-set above your subfloor but it's probably well-supported. Obviously they did not use a Kerdi pan so they must plan to slope the floor somehow with a mud-bed? Off which should not be installed thinner than 1/2" 3/4 of an inch or so.
To fix this I guess they would raise it up and set it on the styrofoam that was provided with the drain. This will change the elevations but that's part of the planning process.
#7 if the drain is at the doorway and the floor slopes up away from the drain towards the back of the shower that is how it is supposed to be, a quarter inch per foot.
__________________
Teddy

Last edited by Elkski; 06-21-2019 at 09:31 AM.
Elkski is offline   Reply With Quote
Unread 06-21-2019, 12:16 PM   #4
KKief
Registered User
 
Join Date: Jun 2019
Posts: 11
Thank you for the responses. Mike, there were 8 empty kerdi-fix bottles in the dumpster (yikes). They are re-doing the shower with the kerdi-band where it's supposed to go.
Teddy, thank you we are addressing the heat cables with matting under it all and buried in thin set. They used the mapei thinset in the shower over the ditra-heat and under the kerdi-membrane. It voids the warranty but so does everything else in there, so if it works and it's only this one part I'll deal with it. We will see what happens with the drain...
Thanks again I really appreciate it.
__________________
Kate
KKief is offline   Reply With Quote
Unread 06-21-2019, 03:33 PM   #5
jadnashua
Veteran DIYer- Schluterville Graduate

STAR Senior Contributor

 
Join Date: Jul 2004
Location: Nashua, NH
Posts: 14,964
Kerdifix IS waterproof. It's a very expensive way to seal joints and screw penetrations. It's the way Wedi does it with a very similar product. I think if you call Schluter, they'll tell you it will work IF there's a continuous coverage. How much overlap they want, I don't remember. One of the instructors said he patched the vinyl liner of his pool with it underwater, without draining his pool. He did use it as the adhesive to hold a vinyl patch in place.

Kerdiband is the much less expensive way to get a waterproof seam. ON a tub/wall junction, their videos show them using a bead of Kerdifix to adhere a strip of Kerdiband to the tub, and thinset to hold it onto the wall, whether that's Kerdiboard or Kerdi.
__________________
Jim DeBruycker
Not a pro, multiple Schluter Workshops (Schluterville and 2013 and 2014 at Schluter Headquarters), Mapei Training 2014, Laticrete Workshop 2014, Custom Building Products Workshop 2015, and Longtime Forum Participant.
jadnashua is offline   Reply With Quote
Unread 06-21-2019, 04:05 PM   #6
makethatkerdistick
Registered User
 
Join Date: Oct 2017
Location: North Texas
Posts: 1,017
If you watch Schluter's video, you'll notice that nowhere do they advertise it as a regular bonding agent between sheets of Kerdi. Seems though that they do approve installations done that way upon request.
https://www.youtube.com/watch?v=ETBJqTwS44w

It might also be of interest to check out the video posted here:
https://www.johnbridge.com/vbulletin...d.php?t=127649

I think the regular thinset plus Kerdiband / Kerdi method that includes the 2 inch overlap is the cheapest and best way to proceed. That's how the system is designed to work. Some Kerdifix in critical spots can't harm if deemed necessary but shouldn't be required. I am a believer in the system and am happy with my two Kerdi showers.
__________________
Wolfgang
makethatkerdistick is offline   Reply With Quote
Unread 06-21-2019, 08:30 PM   #7
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 95,505
Welcome, Kate.
Quote:
Originally Posted by Kate
Bathroom remodel with many mistakes by tile subcontractors-- GC willing to fix them--if I tell him which ones.
You should not be required to point out those areas where manufacturer's recommendations were not followed by your GC's subcontractor, your GC should be showing you how his work meets the manufacturer's requirements. It is his responsibility to correct each and every situation where that is not the case. Following product manufacturer's instructions when installing their products is required by building code.

Your GC knows that, or certainly should. A simple suggestion from you that his tile sub isn't following Schluter's installation instructions should be more than enough input from you to get it all corrected or sufficiently explained to you.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 06-22-2019, 06:39 AM   #8
Elkski
Took the Schluter part 1 class my team won!
 
Elkski's Avatar
 
Join Date: Apr 2007
Location: Wasatch front, Utah
Posts: 848
CX,. It's 2019! You live on planet Earth. System Update needed. Haha.

Kate,. You didn't say what type of material was used to make the slope in the shower? I didn't know the highly modified thinset was used to put on kerdie over the ditra heat. Using highly modified between these layers ( kerdi so large compared to any tile) really has prevented air from reacting with the thinset. I would call mapai about that exact thinset. Mapai also makes unmodified thinsets.
However the drainage bed concerns me the most out of all your issues. If you have slope at all it means some material tapers down to next to nothing at the drain. I'm assuming the drain is on a very thin layer of thinset so maybe 1/4 inch above the subfloor. This junction is not very strong. of course we do not know how that subfloor cutout was supported or how strong your subfloor is. I will feel better if you tell me it was cement but I think you said it was plywood. The flexing right around the drain could cause an issue with the membrane
__________________
Teddy
Elkski is offline   Reply With Quote
Unread 06-22-2019, 08:31 AM   #9
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 95,505
Teddy, the standards of responsibility in the homebuilding industry do not vary with the competence and reliability of the contractors involved. A General Contractor has a fiduciary responsibility to his customers, regardless who is doing the actual work on the project. I don't believe any "System Update" is needed in that arena, thank you.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 06-22-2019, 09:46 AM   #10
Elkski
Took the Schluter part 1 class my team won!
 
Elkski's Avatar
 
Join Date: Apr 2007
Location: Wasatch front, Utah
Posts: 848
I am old-school quality and it's very depressing living with the craftsmanship of workers today. I just don't know how many GC are going to rip up a floor and redo things. At a minimum it's like pushing a rope up the hill and not a good experience in life. For the workers many times doing things the wrong way pays more by the hour.
__________________
Teddy
Elkski is offline   Reply With Quote
Unread 06-22-2019, 10:00 AM   #11
Dave Gobis
da Man!
 
Dave Gobis's Avatar
 
Join Date: May 2001
Location: Racine, WI.
Posts: 5,698
As someone who deals with claims daily for a living, I can state unquestionably it is wrong to assume a GC knows what should and shouldn't happen in sub trades categories.
Dave Gobis is offline   Reply With Quote
Unread 06-22-2019, 12:23 PM   #12
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 95,505
Point taken, Dave, but I still submit that he knows he is responsible for any deficiencies in the work performed.

Teddy, I understand and share your position on the available quality of workers these days, but I still maintain that lowering the standards and expectations is not an acceptable approach to correcting the situation.

For mine own part, I'm just glad I'm no longer in the homebuilding business.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 06-22-2019, 12:50 PM   #13
Elkski
Took the Schluter part 1 class my team won!
 
Elkski's Avatar
 
Join Date: Apr 2007
Location: Wasatch front, Utah
Posts: 848
I think only a small % of consumers are half as educated about tile as the OP. So these tile guys never get called on mistakes. Most homeowners don't care.
Two very recent examples are my brother just built a big house in Denver didn't even want to talk about how they were doing the 3 showers. I have no idea except I know they are very expensive just the glass enclosures are close to $5,000 each I would guess. The kitchen backsplash tiles are hard and fast against the granite.
A man at the poker club didn't even want to talk about water how how he was going to waterproof his durock wallboard in his shower or the shower base or drain.

I dont think that many installers have used linear drains, ditra heat, much less heat in the shower. I'm not sure how the installer didn't know to use kerdi band in the corners but maybe he was told what to do and and supplied materials, obviously had lots of Kerdi fix on the job. To these guys there is no time to go buy some kerdi band or other thing if they forgot something. They just make do because time is money.
__________________
Teddy

Last edited by Elkski; 06-22-2019 at 01:06 PM.
Elkski is offline   Reply With Quote
Unread 06-23-2019, 07:30 AM   #14
KKief
Registered User
 
Join Date: Jun 2019
Posts: 11
"To these guys there is no time to go buy some kerdi band or other thing if they forgot something. They just make do because time is money."

Yes, you nailed it. The tile guys were missing some materials and instead of waiting for the GC to get them, they plowed ahead with the installation so they could get to the next job. There are mistakes on all sides, and I choose the GC so that's on me as well. I am fortunate to have the information and resources available online and your forum to work with them on addressing the issues. If it's not done by the (Schluter) book, but works equally as well, that is an efficient solution for me at this point.

Teddy, the plywood subfloor itself was sloped towards the entrance of the shower and drain. Tilers laid down Schluter all-set, then the ditra mat and the ditra heat cables, then more all-set and tiled over it. There was no Kerdi waterproofing on top of the heat cables in the shower. Those guys refused to re-do it and left. New tiler popped off the old shower tiles, removed as much all-set as possible and tested the ditra cables. Then he put down Mapei Ultraflor Modified Thinset over the ditra heat, followed by Kerdi.

Schluter said--no, using another company's modified thinset would never be advised and voids the warranty, although they could not confirm that it would fail. If anyone has experience with these products failing together, please let me know. This week, new tiler will use Schluter all-set to tile on top of the kerdi. The Mapei will remain between the dirta-heat and Kerdi waterproofing, unless I tell them to re-do.

Because of that extra thinset, the shower floor is higher than it was before, but slopes towards the drain. And it may not be exactly flush to the drain, more like a waterfall. They also said the linear drain was framed and blocked off underneath. The shower drain is directly above a drywalled kitchen ceiling, so if there's even one drop of water everyone will know.

I realize this is not the norm, but I am open to making things work if they actually work. Our house was built in 1925 and this shower was a former closet. Very few good GCs willing to take on this job when they can have their choice of new builds right now.
__________________
Kate
KKief is offline   Reply With Quote
Unread 06-23-2019, 08:14 AM   #15
Elkski
Took the Schluter part 1 class my team won!
 
Elkski's Avatar
 
Join Date: Apr 2007
Location: Wasatch front, Utah
Posts: 848
Does the thinset still feel squishy under the kerdi in the floor? It's probably not thick enough to tell. I just wonder if you get away from the edges if the thinset is still wet and tge kerdi will pull up easily. But maybe it will be ok as is. I'm no expert for sure. I just know if I make a big pile of excess modified thinset the next day there's a thin 1/8 inch crust and it's still soft inside. But it's not like there's any forces pulling your flooring up.

How thick is that plywood subfloor is it two layers?
How did they install that sloped plywood flooring on top of the other flooring? I'm sorry but I just do not get a warm fuzzy feeling about your drain subfloor installation.
Big leaks will maybe show up but it's small ones that don't show up but still cause damage down the road.
You will just have to make a judgment call on what you're comfortable with but I'm pretty sure no one here will say it's done properly.
I am imagining therecare two reasons why Schluter would want Kerdi on top of the ditra heat membrane in a shower 1 is to try to keep that cable dry even though it has insulation. #2 is that the larger thinset cross sections in the ditra heat allows more water seepage which is logical.

I wonder how intact the kerdie membrane has remained theough the tike removal?
You may want to get a mega ohmmeter that checks using a thousand volts to make sure your heating cable has not been compromised. A simple ohmmeter test doesn't really check for pin holes in the insulation that may trip your GFI circuit breaker that the heating system requires.
I'm wondering if they did not have Kerdi band how did they waterproof the wall Kerdi to the ditra heat flooring? Maybe they used Kerdi fix which is not a good method down there.
__________________
Teddy

Last edited by Elkski; 06-23-2019 at 09:06 AM.
Elkski is offline   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Big Mistakes... damsel in distress Cleaning, Restoration and Sealing 4 03-31-2010 12:58 PM
Kerdi Schluter Contractor, Santa Rosa, CA, 60 mi. N of San Francisco chriseu Professionals' Hangout 8 10-19-2009 10:01 AM
mistakes! Aquera Professionals' Hangout 32 03-20-2009 09:44 PM
My Schluter Shower Install - Keeping Tabs on my Contractor Gordo7475 Tile Forum/Advice Board 65 04-16-2008 09:41 PM