Deflection Calculations

I have a floor that spans 11'2" from an exterior block wall to a double 2x12 beam on cinderblock piers spanning 6' apart. I added a 2x10 syp joist to the side of every joist that is beneath the bathroom floor and replaced most of the 3/4" plywood subflooring with advantec and added 1/2" BC spaced 1/8 at all edges and screws 4" at edges and every 6" in the field. My question is what is the deflection of this floor? Deflecto doesn't consider double joist and adding the width to give a single joist width would not be correct I'm sure.
__________________
Gerald
GeraldMadison is offline   Reply With Quote
Sponsored Links
Old 05-09-2019, 08:37 PM   #2
Tool Guy - Kg
Moderator -- Wisconsin Kitchen & Bath Remodeler
 
Tool Guy - Kg's Avatar
 
Join Date: Feb 2005
Location: Oak Creek, WI
Posts: 21,040
Welcome to the forum, Gerald!

I could start giving you some answers making assumptions, but let’s not assume.

What size are your original joists?
Are your original joists the same species of SYP or.....?
What is the O.C. spacing of the original joists?

Tool Guy - Kg is offline   Reply With Quote
Old 05-10-2019, 05:07 AM   #3
PC7060
...unrepentant, detail focused, over-analyzer.
 
PC7060's Avatar
 
Join Date: Jan 2013
Location: Virginia
Posts: 2,675
What Bubbu said... let us know the original size and spacing and we will be a able to give you a reasonable idea of the deflection.

Sounds like you’ve done all the right things so far. Are you planning to put a natural stone on this floor?
PC7060 is offline   Reply With Quote
Old 05-10-2019, 07:14 AM   #4
Kman
Moderator
 
Kman's Avatar
 
Join Date: Nov 2006
Location: NW Arkansas, Ozark Mountains
Posts: 10,699
Quote:
Originally Posted by Davy
Are you planning to put a natural stone on this floor?
Sounds like he's planning on parking a truck on it.

Gerald, the Deflecto may actually do those calculations for you, but like the others said, we don't have the size and spacing of the original joists. If they're also 2x10's, the you would just change the joist width to 3", which is what you have with the doubled up joist now.

That's assuming you sistered it properly, i.e. the sister has to be at least 2/3 the span, it should be glued and nailed/screwed to the original joist, and the original joist is in good shape.
__________________
Kevin

The top ten reasons to procrastinate:

1.
Kman is online now   Reply With Quote
Old 05-10-2019, 09:34 AM   #5
wwhitney
Registered User
 
Join Date: Dec 2015
Location: Berkeley, CA
Posts: 1,065
FWIW, there's a simple formula for determining deflection when you have sistered two different types of joists. Namely, if joist type 1 alone would have deflection L/A, and joist type 2 alone would have deflection L/B, then together they have deflection L/(A+B).

So if your original joist and their sisters have slightly different dimensions, or are different species/quality, you can run the deflectolator twice and add the denominators.

Cheers, Wayne
__________________
Wayne
wwhitney is offline   Reply With Quote
Old 05-10-2019, 11:39 AM   #6
GeraldMadison
Registered User
 
Join Date: May 2019
Location: Juliette GA
Posts: 4
Wow! So many replies and so short of time. The joists are all the same maybe an eighth over 9 in tall. we sistered to every joist from one end to the other with no breaks. All are home runs. We used 3 in screws fastened top and bottom, every 10 in. The joist were originally spaced 16 on Center and we doubled every joist. Most on the same side some on the other due to the fact that there were other things in the way, i.e. Plumbing Etc.. The 3/4 plywood we left in place, we blocked with two-by-fours flat and screwed the subfloor to blocking where there were no t&g. We replaced what we took out with 3/4 inch advantech. We then installed half-inch BC plywood and used inch and 3/4 screws and fastened as mentioned above. I don't know as far as what species the southern yellow pine that we used or what was there to start with but all was in great shape with the exception of one area near the shower where maybe the top quarter inch or so was compromised buy water damage. I started to put 3 in in the deflection calculator but as I understand it a 3 inch solid Timber would be different in its ability to handle a load than two inch and a half timbers fastened together. If that is an incorrect statement then so be it I will just plug in the numbers and see what I get. Thanks to all who replied to my post! I will check back for any additional input.
__________________
Gerald
GeraldMadison is offline   Reply With Quote
Old 05-10-2019, 04:27 PM   #7
PC7060
...unrepentant, detail focused, over-analyzer.
 
PC7060's Avatar
 
Join Date: Jan 2013
Location: Virginia
Posts: 2,675
I ran the numbers on the tools; looks good.

Quote:
Originally Posted by Deflecto
Thank you for using the John Bridge Forums Deflect-O-Lator :-)

For joists that are SYP or Douglas Fir, in good condition, 9 inches tall, 3 inches wide, 16 inches on center, and 12 feet long between supports, the deflection calculated is 0.138 inches.

This translates to a deflection of L / 1043.

Since the maximum deflection for tile is L / 360, and for natural stone is L / 720, your floor is rated for Ceramic tile or Natural stone, Congratulations!
Those results aline with my calculations too.
PC7060 is offline   Reply With Quote
Old 05-10-2019, 04:29 PM   #8
PC7060
...unrepentant, detail focused, over-analyzer.
 
PC7060's Avatar
 
Join Date: Jan 2013
Location: Virginia
Posts: 2,675
Quote:
Wow! So many replies and so short of time.
It’s a good excuse for not doing my labor intensive work!
PC7060 is offline   Reply With Quote
Old 05-12-2019, 08:05 PM   #9
GeraldMadison
Registered User
 
Join Date: May 2019
Location: Juliette GA
Posts: 4
Thanks for the input! I would like to know what, if any, difference there is in solid timbers v/s double or triple joist of the same girth. I just don't see in my pea brain how they could be the same. :
__________________
Gerald
GeraldMadison is offline   Reply With Quote
Old 05-12-2019, 08:12 PM   #10
PC7060
...unrepentant, detail focused, over-analyzer.
 
PC7060's Avatar
 
Join Date: Jan 2013
Location: Virginia
Posts: 2,675
Multiple section beams are treated as a single integrated structure provided the separate elements are attached using approved methods. Could be nails for joists or structural screw for LVL sections; just have to follow the approved schedule.
PC7060 is offline   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Help with thickness calculations of bath tile floor.... Chairandy Tile Forum/Advice Board 3 02-25-2018 07:22 PM
Newbie Deflection and load bearing joist calculations willyoung Tile Forum/Advice Board 3 11-15-2014 10:06 AM
Deflecto calculations Dazed & Confused Tile Forum/Advice Board 3 05-22-2012 07:24 PM
Circle Design Calculations K_Tile Professionals' Hangout 3 09-29-2008 03:51 AM
Deflection rate calculations John Joesph Tile Forum/Advice Board 2 12-01-2002 10:45 PM


All times are GMT -6. The time now is 08:04 AM.


Sponsors

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2019, Jelsoft Enterprises Ltd.
Copyright 2018 John Bridge & Associates, LLC