Unread 08-23-2019, 08:24 AM   #1
Ken C.
Stone Wall on 11 7/8 Joist
I want to add 2500 lbs of stone/mortar to a 14 foot wall on 11 7/8 engineered joists offset 4 feet from the load bearing wall below. The span below is 18 feet. The wall crosses 12 joists with 16" on centre. Is this doable?
Ken
Ken C. is offline   Reply With Quote
Unread 08-23-2019, 10:14 AM   #2
Elkski
Elkski's Avatar
I think you're going to have to talk to a structural engineer on this one
Teddy
Unread 08-23-2019, 01:07 PM   #3
Hi Ken,
It sounds like it'll work. I am not an engineer, though.
How much does the wall weight now?
Unread 08-24-2019, 04:25 AM   #4
Ken C.
Thank you for the reply John. The wall weight I'm not sure, 2X4 studs, 1/2" plywood, 6' pine slab floating shelf. I'll guess about 300 lbs. The 2500 lbs I quoted was a higher than calculated figure as well. I have 126 sq. feet of wall and I weighed 1 sq. foot of the stone I cut from a cliff near my home at 12.5 lb. That would give me a bit of leeway with the weight quoted for mortar.
Ken
Unread 08-24-2019, 07:47 AM   #5
PC7060
PC7060's Avatar
That’s a big span for such a significant load over a concentrated section. I’d give the joist manufacturer a call to get their recommendations before proceeding. What type of flooring is in this room?
Unread 08-24-2019, 09:21 AM   #6
wwhitney
FWIW, if the design total load for the floor is currently 50 psf (40 psf live plus 10 psf dead), then the current maximum moment demand on a joist is 2700 ft-lbs [0.5 * 9 * 9 * 50 * 16/12].
If you add a 200 lb point load to a joist, 4 feet from the end, the maximum moment demand goes up to a bit over 3100 ft-lbs. [The gain is a bit over half of 4 * 200.] That would be about 15% higher.
So you need to find out if there is currently sufficient overcapacity for the increased demand. That means finding either the original engineering for the floor joists, or determining the manufacturer and model of the joists, and checking their literature for the joist capacity, and also determining if 50 psf is the correct current demand.
Cheers, Wayne
Wayne
wwhitney is online now   Reply With Quote
Joist support wall monster2333 Tile Forum/Advice Board 18 07-09-2015 08:00 AM
2nd Floor Wood Joist Deflection issue for Stone Installation ProTech Tile Restoration Tile Forum/Advice Board 6 09-23-2013 06:19 PM
possible to turn wall joist flat tonysg Tile Forum/Advice Board 5 02-25-2009 11:40 PM
Subfloor/Joist stiffening for stone tile geddy2112 Tile Forum/Advice Board 36 02-13-2006 03:17 PM
exterior stone veneer wall on block wall Nicky Tile Forum/Advice Board 3 07-14-2004 03:47 PM