Unread 10-30-2019, 05:37 PM   #1
Scott12345
Registered User
 
Join Date: Oct 2019
Location: Massachusetts
Posts: 8
Preparing an Advantech subfloor

Hi! Planning my first tiling job for the 16’ by 24’ 4” first floor of an early 1900s house. I’ve been through a lot of posts here and I’ve learned a lot. But I still have a few questions!

I’ve reinforced my floor assembly with the help of a structural engineer. Here are the stats:
Joists run 16’ long with OC spacing running between 19” and 25”.
Joists are the original 2 by 6s with new 2 by 8s sistered on. (Only the 2 by 8 makes contact with the subfloor.)
A 6 by 6 beam supports all joists midspan and is supported at each end by the foundation walls and there are three evenly spaced lally columns on concrete pads supporting the center of the beam.
There are two runs of solid blocking 4’ from either joist ends.
I have used subfloor adhesive and ring shank nails to attach ¾” Advantech t&g panels to the joists.

The Deflection calculator (with 8’ joist length and a single Douglas fir joist 1.5” by 7.25” entered) gives me a rating of L / 545 so I think deflection along the length of the joists is more than adequate for porcelain tile.

With my 19”-25” joist spacing Advantech says I should have used their 1 1/8” panel if planning to install tile. Schluter says I could use Ditra XL over my current assembly and be fine. From reading posts here on John Bridge I think screwing down at least 3/8” plywood (per the Woeste and Nielsen article) over the Advantech would be preferred.

I plan to install 12” by 24” porcelain tiles and then install kitchen cabinets over the tile. (Although I did see some good looking 30 by 30 tiles recently…)

My questions:

If the addition of 3/8 ply underlayment is indeed recommended, I could then use regular 1/8” Ditra followed by the tile?

The majority of the subfloor is within the 1/8” or less deviation within 10’. However there are a couple of dips (1/8”-3/16”). Should I fill these dips before or after I screw down the 3/8” plywood underlayment? What type of product could I use? I don't think a SLU over the whole floor is needed, just looking to fill the two or three spots.

Whether I use cement board or Ditra, thinset will go into the 1/8” gaps I leave between underlayment panels. One cement board manufacturer (Wonder board) says to lay a 1 inch “Bond Breaker Tape” over the seams but they offer no suggestions as what tape to use nor do they sell such tape. What is the general practice here? Fill those gaps with thinset or tape over them?

I will install ¼”+ movement joints at the perimeter of the room and at the door sill. With my 16’ by 24’ room do I need a movement joint mid-field? I do have one south facing window in this room.

Thanks for reading this long post, Scott
__________________
Scott
Scott12345 is offline   Reply With Quote
Sponsored Links
Unread 10-30-2019, 06:44 PM   #2
jadnashua
Veteran DIYer- Schluterville Graduate

STAR Senior Contributor

 
Join Date: Jul 2004
Location: Nashua, NH
Posts: 13,201
Finding 3/8" ply that doesn't closely resemble a pretzel or a Pringle chip is hard, although it is the minimum thickness recommended by the TCNA. But, yes, if you can find some that is actually flat (and is made of all plies C or better), it would work. Keep in mind that Advantec is really dense, and screw jacking is a big risk unless you predrill a pilot hole, or the screw has a long enough smooth part to ensure the two sheets get clamped tightly together.

Personally, I'd probably use some floor patching material to fill the low spots and then use the Ditra XL. Your overall floor buildup would be lower, and it would be easier. Not all patching materials are designed for use under tile. If you choose to use the ply, you'll probably find nominal 1/2" material will work better and, you would flatten the surface AFTER you install the ply, as screwing through it could cause it to crack and delaminate.
__________________
Jim DeBruycker
Not a pro, multiple Schluter Workshops (Schluterville and 2013 and 2014 at Schluter Headquarters), Mapei Training 2014, Laticrete Workshop 2014, Custom Building Products Workshop 2015, and Longtime Forum Participant.
jadnashua is offline   Reply With Quote
Unread 10-30-2019, 07:21 PM   #3
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 88,995
I wouldn't bother with anything thinner than nominal 1/2" exterior glue plywood for a second layer of subflooring for the reasons Jim cited. And I'd want a second layer. I know Schluter likes their Ditra XL over single layer subfloor over 24" joist centers, but I wouldn't be comfortable with that. A second layer and regular Ditra would suit me much better.

As for movement accommodation, the industry standards call for joints every 20 to 25 feet for interior installations not subjected to temperature changes of more than 20 degrees F or exposed to moisture, but specify the exterior standard of every 8 to 12 feet for interior installations exposed to direct sunlight. Judgement call on your part.

As for taping the plywood joints, I don't really know if Schluter has a recommendation under Ditra, but for the most part the substrate community seems to think doing nothing at all about those joints on interior installations is acceptable. Don't try to fill them with mortar, don't try not to. A little incongruous among all the other requirements, but we don't seem to hear of problems resulting from the intentional neglect. Certainly no reason not to use bond-breaker tape if it makes you more comfortable. There is such tape out there, but you're not gonna find a lot of pros who can tell you where to get some.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 10-30-2019, 10:54 PM   #4
Kman
Moderator
 
Kman's Avatar
 
Join Date: Nov 2006
Location: NW Arkansas, Ozark Mountains
Posts: 11,086
I wouldn't worry about the plywood joints either, but if I did, I'd fill them with some cheap latex caulk. You just want something to keep the mortar out.
__________________
Kevin

The top ten reasons to procrastinate:

1.
Kman is online now   Reply With Quote
Unread 10-31-2019, 05:20 PM   #5
Scott12345
Registered User
 
Join Date: Oct 2019
Location: Massachusetts
Posts: 8
Thanks for the quick reply and the advice. Much appreciated!

Regarding the "floor patching material" for the dips in my subfloor. Once I've installed plywood underlayment I would apply this material. Something like Ardex Feather Finish or similar?

Thanks again,
Scott
__________________
Scott
Scott12345 is offline   Reply With Quote
Unread 11-01-2019, 05:46 AM   #6
ss3964spd
Moderator
 
ss3964spd's Avatar
 
Join Date: Jul 2005
Location: Fairfax, Va
Posts: 2,516
Send a message via Yahoo to ss3964spd
Yup.

Read the instructions though, because some of those fillers require using their matching primer.
__________________
Dan
---------------------------------------------------------------------------------
If I recall correctly my memory is excellent, but my ability to access it is intermittent.
ss3964spd is online now   Reply With Quote
Unread 11-27-2019, 12:11 PM   #7
Scott12345
Registered User
 
Join Date: Oct 2019
Location: Massachusetts
Posts: 8
Screws

Update: I went to a local lumber yard and bought 15 sheets of 3/8" AC EXT ply. It's been in my house for a week and it's still flat. Yay local lumber yards. (The stuff at HD was in tough shape.)

Deck screws seem to be the recommended screw here but I found Grip-Rite has a "Construction Screws". It's zinc plated and they're about half price of Grip-Rites "Exterior Screws".

As the screw heads are in direct contact with thinset do they need to be rated "Exterior"?

(Another plus of the cheaper "Construction Screw" is that the upper portion is not threaded so I assume no screw jacking and no pre-drilling.)
__________________
Scott
Scott12345 is offline   Reply With Quote
Unread 11-27-2019, 02:26 PM   #8
ss3964spd
Moderator
 
ss3964spd's Avatar
 
Join Date: Jul 2005
Location: Fairfax, Va
Posts: 2,516
Send a message via Yahoo to ss3964spd
I used a whole mess of those zinc plated Grip-Rite construction screws, Scott, they won't be bothered by the mortar. At least one cement board manufacturer allows their product to be installed using aluminum roofing nails, aluminum being a far less noble metal that steel. How often is naked rebar used in concrete? Alla time.
__________________
Dan
---------------------------------------------------------------------------------
If I recall correctly my memory is excellent, but my ability to access it is intermittent.

Last edited by ss3964spd; 11-27-2019 at 02:41 PM.
ss3964spd is online now   Reply With Quote
Unread 11-29-2019, 02:18 PM   #9
Scott12345
Registered User
 
Join Date: Oct 2019
Location: Massachusetts
Posts: 8
Hey Dan, thanks for your quick reply!
__________________
Scott
Scott12345 is offline   Reply With Quote
Unread 11-29-2019, 02:48 PM   #10
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 88,995
Scott, Grip-Rite makes a whole gaggle of different screws. I'm not familiar with one called "Construction Screw," but if it is smaller than #8 I'd not be inclined to use it for your application.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 11-29-2019, 03:27 PM   #11
Scott12345
Registered User
 
Join Date: Oct 2019
Location: Massachusetts
Posts: 8
Hi CX, yes the GR "Construction" screws are #8 1-1/4" Screws so a little bit will pop thru below the subflooring. I've attached a pic of them and the "Exterior" grade screws as well.

I was also looking at the Simpson MTH underlayment screws which are #7 1-1/4". You feel #7 is too small?

I was concerned with any interaction between the metal and the thinset. Didn't want the screw heads to corrode out ten years down the road.

Thanks, Scott

Name:  GR_Construction.jpg
Views: 77
Size:  96.1 KB

Name:  GR_Exterior.jpg
Views: 76
Size:  116.2 KB
__________________
Scott
Scott12345 is offline   Reply With Quote
Unread 11-29-2019, 03:44 PM   #12
Scott12345
Registered User
 
Join Date: Oct 2019
Location: Massachusetts
Posts: 8
Better picture, hopefully the right way around.

Name:  GR-Screws.jpg
Views: 78
Size:  41.9 KB
__________________
Scott
Scott12345 is offline   Reply With Quote
Unread 11-29-2019, 06:59 PM   #13
cx
Moderator emeritus
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 88,995
Scott, I looked in my tool trailer and my boxes of DeckMate 1 5/8ths" and 1 1/4" screws are all #7. The GripRite I have in 1 1/4" are not marked at all for diameter, but appear to be either #7 or #8, but my eye is not sufficiently calibrated to determine for sure. I'd be inclined to think that the Simpson #7s would be adequate on accounta Simpson has been in the framing fastening game for a long time.

I'd need to actually see the screws out of those GripRite boxes you've pictured to tell how significant the difference might be. I'm inclined to think that two "similar" screws from the same manufacturer with nearly a 2x price difference would not be interchangable, eh?

As for the type of coating, all of them except stainless steel are prone to some rust at some point, but anything I've ever used that said "plated" or "Coated" would be adequate to your application.

As for length, if you're fastening 1/2" plywood to 3/4" plywood, your 1 1/4" screws are not technically long enough even if both panels are nominal sizes. The requirement is that the screw, in the shaft diameter, fully penetrate both layers. That means you should have all the tapered part of the screw exposed under the first subfloor layer. The 1 5/8ths" lengths you find in those screw types would be my first choice for your application. Can you get by with the 1 1/4" screws? Probably, but the plywood industry won't be your friend. You'll likely also strip out more screws than you would with the longer screws and you'll need to use more care in getting the heads flushed.

If you don't allow the Tile Ranger to see the underside of your floor, he'll never know what you did and it's unlikely the Plywood Ranger, if there is one, will likely never come by your place.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Unread 11-29-2019, 07:09 PM   #14
Davy
Moderator -- Mud Man
 
Davy's Avatar
 
Join Date: Jan 2003
Location: Princeton,Tx.- Dallas area
Posts: 32,015
Plywood Ranger? Someone else I have to watch out for.
__________________
Davy

www.davystephenstile.com
Davy is offline   Reply With Quote
Unread 11-29-2019, 07:48 PM   #15
smifwal
Registered User
 
Join Date: Mar 2016
Location: Kansas City
Posts: 1,119
I personally don't like the $29 ones the they don't have enough thread. No matter what the screw is doing I want it to have threads nearly to the top. I have used both #7 (bought by mistake)and #8. I use #8 1 3/4 to fasten down 3/4 in subfloor, for all my flooring projects no matter what finished material is going in . I screw down every floor I touch
__________________
Shawn
smifwal is online now   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Advantech Subfloor awhiteman28 Tile Forum/Advice Board 8 03-06-2017 01:55 PM
Advantech subfloor supplier in So. Cal / San Diego? Helmy Tile Forum/Advice Board 9 02-20-2017 07:13 PM
Subfloor/tile options with Advantech TJC Tile Forum/Advice Board 6 01-13-2011 09:38 PM
Preparing Subfloor for Backerboard DIYMaryland Tile Forum/Advice Board 4 03-25-2007 04:53 PM
preparing subfloor stevo Tile Forum/Advice Board 6 01-12-2004 08:18 PM


All times are GMT -6. The time now is 08:40 AM.


Sponsors

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2020, Jelsoft Enterprises Ltd.
Copyright 2018 John Bridge & Associates, LLC