Mmmm. 14" I joist with a 2" flange, 16" oc, spanning 23 feet and you're getting a deflection rating better than L/1100? Mmmm.
You still have the between-joist deflection to deal with, Corby, and you'll not get it with a single layer of 3/4" plywood even at 16" spacing. You'll also have the problem over the joists where there is a joint in that subflooring layer, as Steven is pointing out. You must have a double layer of plywood for
any natural stone installation and it should always be installed following
these guidelines. Some substrate manufacturers will allow a 3/8" second layer with your joist spacing, but I wouldn't install less than half-inch.
Read all of that article and perhaps it will clear up some of the doubt you expressed in your earlier PM. It explains the reasoning pretty well, I think.
You also get into another area of consideration with that long span you have where, even though you meet the deflection standards, the span is so long that the curvature of the floor with the allowable deflection begins to be a factor.
You're gonna need a really good subfloor installation and a real good decoupling membrane over it to have a good chance at a successful installation there.
Do tell the name and model number of those joists, please.