Gut and remodel masterbath with curbless shower

Hello everyone,

Sorry for the long post below but I thought I'd be as detailed as possible right from the begining. I've been lurking and reading these boards for months while planing my masterbath remodel. Unfortunately the more I read, the more options become availabe for doing everything and ends up becoming very confusing. Or perhaps I'm suffering from paralysis by analysis. So I've decided to post my project and get some advise. I have to do this mostly on my own except where absolutely necessary due to budget constraints. I've never tiled before but I'm quite handy. Please refer to the 5'x12' bath in the attached file.

Project:
  • 5' x 12' masterbath including 5' x 3' curbless shower (no bath tub), over an unconditioned garage
  • Subfloor is 3/4" plywood, 16" OC joists running length wise. I have accesss to sister the joists
  • 1/8" Floor warming cables by HeatTech in entire bathroom including shower
  • 12" x 24" x 0.35" (approx. 3/8") porcelain tiles
  • Planned floor installation: Heating cable >> SLC >> Thinset >> Ditra >> Thinset >> Tile
  • The shower stall will be waterproofed with a painted membrane - RedGard or Hydroban (not using Kerdi or similar) extending 12" into the non-wet area. Shower will be prepped for future steam shower. I plan on following the directions here: Mr. Money Mustache (mrmoneymustache.com/2012/12/21/how-to-make-a-relatively-sweet-shower-cheap/)
  • 60" Linear drain, ProLine by QuickDrain, against shower wall opposite glass entry wall\door. Drain installed flush with subfloor with 2% rise to entry
  • Surface mounted shower panel
  • Master bedroom floor height is 3/4" (I'd prefer the bathroom to be flush with it)
  • Minor corrections to the floor plan: Entry door is a pocket door, shower entry swing out glass door and glass panel, shower panel is on the long wall 24" from the right wall

My questions:
  1. How do I install the bath tile flush with the bedroom hardwood floor (3/4")? All the calculations I have done using the installation method above puts the bath floor at a minimum of 15/16". The assumption here is 1/4" SLC + 1/8" Ditra + 3/16" thinset +3/8 tile. How can I shave off an additional 3/16"?
  2. Can I tile directly to the SLC or is there a substitute for Ditra without the 1/8" buildup?
  3. Do I have to use a lath (e.g. Mapelath) with the SLC? How thick is the Mapelath?
That is the question that is currently preventing me from moving ahead with the project so any help is greatly appreciated. I'm sure I will have many more questions as I progress. Thank you all very much for this great resource.

Regards,
-Sri
Attached Images
 
__________________
Sri

Last edited by sri; 08-17-2013 at 08:19 PM. Reason: Correcting items in the floor plan.
sri is offline   Reply With Quote
Sponsored Links
Unread 08-17-2013, 08:26 PM   #2
chuck stevenson
Contractor -- Schluterville Graduate
 
Join Date: Aug 2006
Location: Columbus, Georgia
Posts: 2,248
Welcome Sri,

Have you checked your joist structure using "Deflecto" in the dark blue banner above?

Builders often label space over a garage a "bonus room", meant for light storage or a living space but not much more.
__________________
Chuck

No curb, walk-in shower.
chuck stevenson is offline   Reply With Quote
Unread 08-17-2013, 10:35 PM   #3
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Hi Chuck,

I did check Deflecto. It passes if I sister the joists and I plan to do that. The space is actually the current masterbath and the adjoining walk-in closet. We've combined them to make a slightly larger MB. Actually I have a full unfinished basement and the garage is a part of it.
__________________
Sri
sri is offline   Reply With Quote
Unread 08-18-2013, 09:55 AM   #4
MDtile
Registered User
 
Join Date: May 2013
Posts: 1,360
Is it possible to omit the SLC and set the Ditra directly over the heating cable? Excuse me if this is technically wrong, I generally am not involved with Ditra, preferring Latacrete's new Strata Mat.
MDtile is offline   Reply With Quote
Unread 08-18-2013, 12:08 PM   #5
John Bridge
Mudmeister
 
Join Date: Mar 2001
Location: Rosanky, Texas
Posts: 67,658
Send a message via AIM to John Bridge
Hi Sri,

When using Ditra the order is wood, heat mats, thinset, Ditra, tile. I think this would also apply to heating wires.
John Bridge is offline   Reply With Quote
Unread 08-18-2013, 12:33 PM   #6
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Thanks for the response John. That was the order in which I was going to install. However, my question is how to match the 3/4" floor height in the master bedroom. It seems that I'm going to be 3/16" over on the tile side.
__________________
Sri
sri is offline   Reply With Quote
Unread 08-24-2013, 11:24 PM   #7
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Solved the problem with the floor height difference. I'm going to be using RPM mats for the radiant cables and this will replace the Ditra layer. So 5/16" RPM mat and cable filled with SLC, then RedGard or HydroBan, then thinset and tile should keep me at 3/4". If anyone has any experience or tips for using the RPM mats for radiant heat cable, I'd appreciate it. Thanks.
__________________
Sri

Last edited by sri; 08-24-2013 at 11:36 PM. Reason: Added question.
sri is offline   Reply With Quote
Unread 08-24-2013, 11:33 PM   #8
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Water supply line size to shower panel

I will be using a shower panel (not picked one out yet) with multiple functions instead of individiual assemblies for the shower. The inlets on the shower panel are normally 1/2". I have 3/4" PEX for the main supply line. Should I run 3/4" PEX (about 5 feet) to the shower panel (witha reducer before the panel) so that I can have decent volume with several functions running simultaneously? Or is that short run insignificant or is this thsi unnecessary since the shower panel is all 1/2"? Thanks.
__________________
Sri
sri is offline   Reply With Quote
Unread 08-25-2013, 08:52 AM   #9
cx
Da Home Builder
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 88,267
I wouldn't worry about that last five feet, Sri , I'd run whatever is most convenient at the time.

Chances are your PEX tubing and fittings are of substantially smaller ID than copper or iron pipe and you'll have reduced flows anyway, but reducing from "nominal" three-quarters to nominal half-inch five feet further up the line isn't likely to be noticeable.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 09-20-2013, 12:39 AM   #10
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Is it advisable to drill pipe holes after installing tile?

I am thinking of drilling holes for my water supply lines in the shower wall for the shower panel after waterproofing and tiling since I have access to the exposed wall on the other side to run the lines. Also I will have more control of the position of the holes in the tile this way. Is this advisable? Or should I just make a best guess and install the nipples first? I guess on drawback is that I won't be able to waterproof the pipe holes behind the tile if I tile first. Thanks.
__________________
Sri
sri is offline   Reply With Quote
Unread 09-20-2013, 04:40 PM   #11
Tiger Mountain Tile Inc
Registered Muser
 
Tiger Mountain Tile Inc's Avatar
 
Join Date: Feb 2011
Location: Issaquah, Washington
Posts: 6,619
Hi Sri,

I just looked at your original post and I have some concerns about the plan.

You mention that you are going to prep the shower to be a future steam shower and that you want to waterproof the shower with a liquid membrane. If it's going to be a steam shower I would advise not using a liquid and instead switching to a sheet membrane such as Kerdi or Nobleseal TS to name but two. The liquids just don't have the vapor protection needed for a steam shower.

The other thing is that in the link that you mentioned, How to make a relatively sweet shower for cheap, I can't figure out what the guy did for a drain. Maybe some of the other guys on here can take a look. It doesn't look like a regular 3 piece drain and he didn't use a divot. If the drain isn't correct I would advise you to follow a different method, maybe like this one with a proper shower drain.

Looks like a fun project, though.
__________________
Jim Upton
DIYTileGuy
Tiger Mountain Tile Inc is offline   Reply With Quote
Unread 09-20-2013, 08:24 PM   #12
cx
Da Home Builder
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 88,267
Sri, I'd abandon the idea of plumbing your walls after your shower is tiled. But it's your shower.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is online now   Reply With Quote
Unread 09-20-2013, 10:00 PM   #13
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Is it advisable to drill pipe holes after installing tile?

CX,

Could you please expand on why it's not advisable to plumb after tiling? Is it a waterproofing issue? Thanks.

-Sri
__________________
Sri
sri is offline   Reply With Quote
Unread 09-20-2013, 11:30 PM   #14
sri
Registered User
 
Join Date: Aug 2013
Location: Huntersville, North Carolina
Posts: 29
Gut and remodel masterbath with curbless shower

Jim,

Thank you for your observations. I palnned to follow the directions in the Money Moustache blog to build the shower pan except i will be using the ProLine linear drain by QuickDrain. So the slope is only in one direction to the drain. The drain has a sheet membrane attached to the flange. The sheet will be overlapped with the liquid membrane.

I suppose I might have to reconsider using a liquid membrane if it does not meet the perm requiremets for vapor retardation. Anyone else have an opinion about this with regard to cost to apply sufficient coats of a liquid membrane to achieve the same perm rating as Kerdi DS for example? I was considering a liquid membrane mainly for cost and ease of applicaiton.
__________________
Sri
sri is offline   Reply With Quote
Unread 09-21-2013, 08:09 AM   #15
Tiger Mountain Tile Inc
Registered Muser
 
Tiger Mountain Tile Inc's Avatar
 
Join Date: Feb 2011
Location: Issaquah, Washington
Posts: 6,619
Sri, it can't be done. The liquids can't compete with the sheet membranes as far as vapor perm ratings go.

I forgot that you were using a linear drain. Since you'll probably end up going with a sheet membrane it might be a good idea to explore the linear drains that come with that particular system for example the Schluter Kerdi-line drain or Noble Freestyle linear drain.
__________________
Jim Upton
DIYTileGuy
Tiger Mountain Tile Inc is offline   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Another Masterbath Remodel campmi Tile Forum/Advice Board 98 08-09-2011 06:48 PM
Joe's Masterbath complete gut and reno JJHandyman Tile Forum/Advice Board 43 04-08-2011 10:10 AM
Curbless shower remodel in Hollywood, Ca. Seyma Professionals' Hangout 9 09-17-2008 07:23 PM
Bob's Curbless Shower Bathroom Remodel Bob V. Tile Forum/Advice Board 33 09-15-2008 06:42 PM
Bath Remodel, Curbless Shower hopes, lookin for some help! markeyro Tile Forum/Advice Board 5 01-07-2007 12:21 PM


All times are GMT -6. The time now is 04:38 PM.


Sponsors

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2019, Jelsoft Enterprises Ltd.
Copyright 2018 John Bridge & Associates, LLC