Trying to repair bad moisture problem in the clubhouse. Builder used 1x1 tile through out steam room, tile benches and two steam ports, they used durock (at least it looks like that) sloped ceiling. I know, not needed, I looked through the drop ceiling, there is a poly vapor barrier on top which is completely wet under it so the steam is wicking through the grout and through the durock walls, they are getting mold on opposite sides under the wall paper. Carpet is wet ....steam room has one heavy framed glass door similar to entrance door with no transom and no vent system. Steam runs all day for club members. I need to repair the problem. I think I will have to tear down the whole job seal durock and seal tile will that do the trick since it will be wet from morn. till night....any help thanks so much
Drew
__________________
Drew

Last edited by drewmon; 10-12-2009 at 08:44 PM.
drewmon is offline   Reply With Quote
Sponsored Links
Old 10-12-2009, 09:28 PM   #2
silvercitytile
Registered User
 
silvercitytile's Avatar
 
Join Date: Nov 2007
Location: silver city
Posts: 5,973
Send a message via MSN to silvercitytile
well drew i think u'll have to tear down the whole thing and see what else is going on, dont want to repeat the same thing they did.
__________________
jeff aka papi chulo. "I'll make you famous!"(William H. Bonney aka Billy The Kid)

Schluter Kerdi and Ditra installer in Southern New Mexico
Castillo Construction
silvercitytile is offline   Reply With Quote
Old 10-12-2009, 10:05 PM   #3
custombuilt
Tile and remodeling contractor
 
Join Date: Jan 2007
Location: Quincy, IL
Posts: 2,794
yep tear it all down and build it with Kerdi, or Laticrete's system.
__________________
---------------------------------------------------
Jason W.

Superior Construction
Custom Interior and Exterior remodeling experts
Quincy, IL
custombuilt is offline   Reply With Quote
Old 10-12-2009, 10:16 PM   #4
cx
da Home-builder -- Moderator-at-Large
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 85,153
Welcome, Drew. If you're in the tile trade, helps to add a little biographical information to your Profile so folks can see what it is you do and in what part of the world you do it.

Quote:
Originally Posted by Drew
they used durock (at least it looks like that) sloped ceiling. I know, not needed,
Not sure which part you're indicating is not needed there. They did need some sort of approved wallboard, and they did need a properly sloped ceiling, and seems they had both.
Quote:
Originally Posted by Drew
there is a poly vapor barrier on top which is completely wet under it so the steam is wicking through the grout and through the durock walls,
Steam is a vapor, doesn't need to do any wicking. Will happily pass through the grout and the CBU. If there is an excess of condensation on the inside face of the vapor barrier, it's doing its job, but that would indicate a probable lack of adequate insulation above the ceiling and behind the walls. You check for that?
Quote:
Originally Posted by Drew
they are getting mold on opposite sides under the wall paper. Carpet is wet
Would indicate to me that they really don't have an actual vapor barrier behind the CBU walls there. Shouldn't be that kind of moisture entering those wall cavities if the vapor barrier was properly installed.

You'd need a good deal more information to determine if that's repairable at all, I think, and I doubt you can do much with it short of a compete tear-out and re-do.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Old 10-12-2009, 10:23 PM   #5
GraniteGirl
Ms. Makita
 
GraniteGirl's Avatar
 
Join Date: Dec 2004
Location: Maple Bay, BC (On beautiful Vancouver Island!)
Posts: 2,384
Send a message via Yahoo to GraniteGirl
Quote:
Originally Posted by Drew
seal durock and seal tile will that do the trick
What cx said about finding the true cause of their problems, and no - sealing alone will not solve whatever is ailing the steam room.

Sounds like there is a whole list of wrongs with the place.
__________________
Adriana

www.IslandSoapstone.com

Relax - it's a rock! What could go wrong?!

GraniteGirl is offline   Reply With Quote
Old 10-13-2009, 01:43 AM   #6
Shaughnn
Trowel Monkey
 
Shaughnn's Avatar
 
Join Date: Jan 2004
Location: Kent, Washin'ton
Posts: 11,467
Pull the plates off of all of the penetrations and check for proper sealing there before you crack into the walls. It's my belief that you should tear the whole thing out as there will be no way at all to ensure that you've tackled the mold issue until you've exposed everything touching this steamer.
Rebuild it with KERDI, Noble or WEDI with a coat of Aquafin's "Vaportight" . Since it's a commercial steamer, I don't know for certain that any of the other manufacturers will offer a warrantee without a whole bunch of teeny-tiny asterix.
Best of luck,
Shaughnn
Shaughnn is offline   Reply With Quote
Old 10-13-2009, 06:03 AM   #7
Brad Denny
Tile Contractor Nashville, TN
 
Brad Denny's Avatar
 
Join Date: Mar 2007
Location: Joelton, TN
Posts: 4,160
Hi Drew,
Being the guy to fix something like this can be a great opportunity or your worse nightmare, depending on the depth of the client's pocket. To properly fix the problem, starting from scratch is the only real option. Here are a few links to manufacturers who suggest their product for steam showers. The Schluter link is actually an article that you could pass along to the client to explain what needs to be done to ensure that the problem will not arise again.


http://www.laticrete.com/Homeowners/TechnicalDesignManuals/TiledSteamRoomDesignManual/tabid/1686/Default.aspxhttp://

http://www.noblecompany.com/Portals/...out1%20(1).pdf
http://www.schluter.com/5232.aspx

I say that it could be a nightmare if the "Country Club" only wants to "patch it up". There's not a lot you can do here without covering yourself via documentation clarifying that you have informed them of what needs to be done, and aren't responsible for what you did do.
__________________
Brad


Brad Denny is offline   Reply With Quote
Old 10-13-2009, 09:42 AM   #8
cx
da Home-builder -- Moderator-at-Large
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 85,153
I think in that application, Shaughnn's suggestion of the Noble product would be your best bet. They've got sheet membranes that are very close to vapor proof. The Kerdi is also a technical vapor barrier, having a perm of only about 0.7, I believe, but the Noble TS is in the range of 0.05 as I recall. Not much vapor going through that in service.

The steam shower you're describing could not have been built to any standard I've seen published. There is just no effective method of making a vaporproof box using CBU with a poly sheet behind it. Too many fastener penetrations of the membrane, to begin with.

A CBU box can be made substantially vaporproof using a sheet membrane over the entire interior and properly sealing all plumbing and other penetrations. That's the direction I'd look in replacing that failed system. You could also eliminate the traditional pan and liner using the surface-applied membrane. Another big plus in my book.

Gotta agree with Brad's assessment of the possible/probable quagmire associated with just trying to fix what's there. Even the proper application of a vapor barrier on the existing interior leaves you with all sorts of mold problems behind the walls and ceilings - and the floor, for that matter. Don't think I'd wanna be involved in anything like that in today's litigious climate.

My opinion; worth price charged.
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Old 10-13-2009, 10:34 AM   #9
e3
Registered User
 
Join Date: Jan 2003
Location: mi.
Posts: 4,666
Send a message via Yahoo to e3
we have formed a committee to "re-write" the steam room details for the TCNA Handbook.
The first thing I would suggest is, if there is a Arch. or design pro. have them make the reccomendations. Some one needs to know, what membrane,how much insulation,type of door ,the lights,ect ect....
You are looking at a DO -OVER from what I have read.
__________________
Eric
Mapei USA
e3 is offline   Reply With Quote
Old 10-13-2009, 10:58 AM   #10
cx
da Home-builder -- Moderator-at-Large
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 85,153
Quote:
Originally Posted by e3
we have formed a committee to "re-write" the steam room details for the TCNA Handbook.
That will be a most useful undertaking, Eric. Maybe we can start a thread about that like James started about revisions to the movement joint standards?

I know y'all prolly have more input at this point than you can stand, but you never know when someone out there in Real World Land might come up with a little pearl of wisdom that's been overlooked, eh?
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Old 10-13-2009, 01:05 PM   #11
John Bridge
Mudmeister
 
Join Date: Mar 2001
Location: Houston, Texas
Posts: 66,621
Send a message via AIM to John Bridge
I second the Handbook thread idea. Will you start it, Eric?
John Bridge is offline   Reply With Quote
Old 10-13-2009, 01:11 PM   #12
cx
da Home-builder -- Moderator-at-Large
 
cx's Avatar
 
Join Date: Jul 2001
Location: Boerne, Texas
Posts: 85,153
Tryin' to get holt of James to conjure up a "standard" heading for these therads that concern the Standards Committee subjects, but he ain't answerin' his mail.

I'd like something that identifies them as that kinda thread with particular subject after that.

Like, maybe, Technical Discussion - Steam Shower. Or some such.

Help us think of somethin' catchy, Eric. Somethin' other than Noble, eh?
__________________
CX

Y'ALL NEW VISITORS READ THIS HERE!
cx is offline   Reply With Quote
Old 10-13-2009, 01:57 PM   #13
dhagin
builder, anti-builder, rebuilder -- Moderator
 
Join Date: Mar 2009
Location: oahu
Posts: 13,077
Quote:
Originally Posted by Eric
The first thing I would suggest is, if there is a Arch. or design pro. have them make the reccomendations. Some one needs to know, what membrane,how much insulation,type of door ,the lights,ect ect....
Excellent idea, couldn't have said it better myself.
__________________
dana

"the road to hell is paved with osb, mastic, pre-mixed latex 'grout' or 'thinset', "
dhagin is offline   Reply With Quote
Old 10-13-2009, 02:51 PM   #14
tilejoe
Registered User
 
tilejoe's Avatar
 
Join Date: Sep 2008
Location: Allentown, Bethlehem, Easton, PA
Posts: 2,302
I know this doesn't help much, but I remember a prominent voice in this industry replying to the question of what to do for a commercial steam room, he said "don't do it, just stay away.."

like i said, not much help...

__________________
Joe Lenner

Infinite Ceramic & Stone
www.infiniteceramic.com
NTCA Pennsylvania State Rep
CTEF Certified Installer #769
tilejoe is offline   Reply With Quote
Old 10-20-2009, 09:04 AM   #15
olzo55
Guest
 
Posts: n/a
Eric, why does the membrane go behind the cbd for the ceiling?

olzo
  Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Tiling the kitchen at the Archery club? Ditra? Elkski Tile Forum/Advice Board 24 09-29-2007 11:15 AM
decided on deck mud....Can I join the club now?! cats4nat Tile Forum/Advice Board 2 11-16-2005 09:59 AM