Ditra Duo Thermal Break. Is it worth it?

A buddy is wanting heated flooring in their master bedroom and bath. They are using ditra heat. It's being installed on a concrete slab. The question. Is there a noticeable heat wise difference between using the ditra heat duo vs the regular ditra heat.
Electricity usage isn't an issue. They are hoping for faster heat up time and heat retention.

Thanks

I am neither clever nor funny
__________________
Travis
Shady at Best is offline   Reply With Quote
Sponsored Links
Old 09-15-2017, 03:36 PM   #2
wwhitney
Registered User
 
Join Date: Dec 2015
Location: Berkeley, CA
Posts: 757
Schluter thinks so:
Quote:
Originally Posted by Schluter Ditra Heat Data Sheet
In laboratory testing, DITRA-HEAT-DUO reduced floor warming response time from 68F (20C) to 78F (25.5C) by approximately 80% (90 minutes) compared to DITRA-HEAT over a concrete substrate. Wood substrates act as insulators and typically do not pose the same challenges as concrete substrates. In the same laboratory testing, DITRA-HEAT-DUO only reduced floor warming response time from 68F (20C) to 78F (25.5C) by approximately 20% (5 minutes) compared to DITRA-HEAT over a plywood substrate. Schluter-DITRA-HEAT-E-HK heating cables were spaced at three studs in all of the above tests. Results above are based upon laboratory testing. Actual results may vary depending on various factors, including concrete substrate thickness, concrete substrate temperature, room temperature, heat losses, etc.
Cheers, Wayne
__________________
Wayne
wwhitney is online now   Reply With Quote
Old 09-15-2017, 05:28 PM   #3
Shady at Best
Tyrone shoelaces
 
Shady at Best's Avatar
 
Join Date: Apr 2014
Location: las cruces new mexico
Posts: 420
Thanks. But i don't trust what schluter says. Plus, i called schluter and the girl said things that contradict what the website says.

Has anyone physically noticed a difference between the products

I am neither clever nor funny
__________________
Travis
Shady at Best is offline   Reply With Quote
Old 09-15-2017, 06:22 PM   #4
lati_cz
michal
 
Join Date: Nov 2008
Location: sunnyvale, ca
Posts: 1,857
Years ago I did few bathrooms in a house, there was one in basement on slab. There was significant difference in time of heating up, on slab took much longer than on plywood. It was Neuheat mat.
__________________
Michal
lati_cz is offline   Reply With Quote
Old 09-15-2017, 08:24 PM   #5
HS345
Tile Contractor
 
HS345's Avatar
 
Join Date: Jan 2007
Location: Sherrodsville, Ohio
Posts: 6,464
Quote:
Originally Posted by Travis
But i don't trust what schluter says. Plus, i called schluter and the girl said things that contradict what the website says.
Could you tell us exactly what contradictory things she said?
__________________
The name's Greg
HS345 is offline   Reply With Quote
Old 09-16-2017, 09:36 AM   #6
Tiger Mountain Tile Inc
tile lackey
 
Tiger Mountain Tile Inc's Avatar
 
Join Date: Feb 2011
Location: Issaquah, Washington
Posts: 6,366
Looks like they've changed the name of it. It used to be called Ditra-Heat TB (thermal break). Anyone know if there's been tweaks to the actual product?

Here's a very unscientific opinion: I've used this stuff and it's noticeably thicker and has a thick fleece on the bottom of it. So based only on the way the product looks- I would guess that there's something to Schluter's claim.

Name:  2017-09-16 07.33.45.jpg
Views: 356
Size:  18.1 KB
__________________
Jim Upton
DIYTileGuy
Tiger Mountain Tile Inc is offline   Reply With Quote
Old 09-16-2017, 01:03 PM   #7
Shady at Best
Tyrone shoelaces
 
Shady at Best's Avatar
 
Join Date: Apr 2014
Location: las cruces new mexico
Posts: 420
Quote:
Originally Posted by HS345 View Post
Could you tell us exactly what contradictory things she said?
The person said that there is really no difference in warm up times, no noticeable difference on concrete, that duo is not intended intended to be installed on 2nd story's or wood foundations, although it acts as a sound damper on second stories.
She said that the only thing that it does is blocks a percentage of the heat from transferring to the slab.

I think there were a few other things but i stopped paying attention when i realized that the person didn't know what they were talking about.


I am neither clever nor funny
__________________
Travis
Shady at Best is offline   Reply With Quote
Old 09-17-2017, 01:00 PM   #8
tilemanct
Tile & Stone
 
Join Date: Sep 2002
Location: Northeast/Connecticut
Posts: 2,255
Remember the physics of radiant heat. Heat goes to cold. On a slab, the radiant will travel to the cold and equalize before progressing upwards. A barrier will help but in reality you would need a minimum of 2" for it to be noticeably effective. There was a product we used to use with NuHeat from Midwest products called Insulament that is similar to what's on the back of the Ditra Heat mat. It helped a bit.
__________________
Dave

CTEF Certified Installer
I lost my hero on 5-21-16 You will be missed. Semper Fi
tilemanct is offline   Reply With Quote
Old 09-17-2017, 05:21 PM   #9
wwhitney
Registered User
 
Join Date: Dec 2015
Location: Berkeley, CA
Posts: 757
Quote:
Originally Posted by Dave
On a slab, the radiant will travel to the cold and equalize before progressing upwards.
It's not quite that simple. Warm up time is definitely a dynamic process, not an equilibrium process.

Heat from the wire will migrate in all directions via conduction, according to the R-values of the materials involved. Concrete has a very low R-value, so it will transfer heat very well. Inserting a small layer of material with a higher R-value can make a significant difference in how much heat initially goes downward rather than upward to heat the surface of the tile.

Cheers, Wayne
__________________
Wayne
wwhitney is online now   Reply With Quote
Old 09-17-2017, 09:14 PM   #10
Lmcabinets
Registered User
 
Lmcabinets's Avatar
 
Join Date: Oct 2013
Posts: 4
Ditra TB

Electric heat will heat the floor without the "TB" but the cost of running the system will be higher because the concrete will be sucking heat and costing money.
__________________
Kevin
Lmcabinets is offline   Reply With Quote
Old 09-18-2017, 03:56 PM   #11
tilemanct
Tile & Stone
 
Join Date: Sep 2002
Location: Northeast/Connecticut
Posts: 2,255
Wayne from experience (had Nuheat on basement floor) with a similar material that is under the Ditra Heat Mat, it took forever to warm the floor and the electric bill was quite steep.
In house two I wised up and did 4" rigid insulation with hydronic radiant in slab. I also made sure there was lots of drainage pipe under slab.
So economical to run and the comfort is out if this world.
__________________
Dave

CTEF Certified Installer
I lost my hero on 5-21-16 You will be missed. Semper Fi
tilemanct is offline   Reply With Quote
Old 09-18-2017, 04:49 PM   #12
wwhitney
Registered User
 
Join Date: Dec 2015
Location: Berkeley, CA
Posts: 757
Dave I don't doubt that using Ditra Heat Duo on a concrete slab on grade without any insulation underneath will take forever to heat up and will use alot of electricity. Plain Ditra Heat would probably take two forevers and cost twice as much. :-)

Basically, electric resistance heat on an uninsulated slab on grade is a bad application. The thin insulation layer on Ditra Heat Duo will make it slightly less bad.

Cheers, Wayne
__________________
Wayne
wwhitney is online now   Reply With Quote
Old 09-27-2017, 06:02 PM   #13
Shady at Best
Tyrone shoelaces
 
Shady at Best's Avatar
 
Join Date: Apr 2014
Location: las cruces new mexico
Posts: 420
Anyone notice hollow sounding tiles when setting on top of ditra heat duo.
Thinset is both schluter ditra set, and ardex x5. Tiles are back buttered. No difference in sound been between the 2 different thinsets.


I am neither clever nor funny
__________________
Travis
Shady at Best is offline   Reply With Quote
Old 10-23-2017, 04:44 PM   #14
Diaz.victor@aol.com
Central Florida Tileguy
 
Join Date: Jul 2016
Location: Central Fl
Posts: 43
hollow tiles on ditra heat

" i just installed a 500 sq ft master bathroom floor with pan included
and yes the entire floor sounds terribly hollow i used a 1/4" trowel and mixed the thinset a little wetter than normal to be sure it stuck well and after installing and grouting floor i noticed that its scary hollow
i know that i installed everything properly but im still not comfortable with how the floor sounds need to talk to a rep about this
__________________
Victor
Central Florida Tileguy
Diaz.victor@aol.com is online now   Reply With Quote
Old 10-24-2017, 04:15 PM   #15
South land Tile
Registered User
 
Join Date: Oct 2015
Location: Greenville, Ms
Posts: 105
I think schluter changed something with the backing on the ditra heat membrane awhile back cuz it's a pain in the neck to get thinset transfer on it now.
Awhile back I had to pull up a whole room of it that I had put down with ditra set mixed to the correct consistency for applying membranes because it just didn't bond.
Last job I did with ditra heat I used laticrete 254 to bond it to the slab worked a lot better but it was breaking the rules
__________________
Charles
South land Tile is online now   Reply With Quote
Reply

Stonetooling.com   Tile-Assn.com   National Gypsum Permabase


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Advice for thermal break bmlant Tile Forum/Advice Board 7 08-12-2015 03:11 PM
thermal break when using RPM mats bxd20 Tile Forum/Advice Board 10 11-25-2013 09:09 AM
Thermal break for slate on slab Skivvt Tile Forum/Advice Board 8 06-05-2013 07:42 AM
slab thermal break jwmezzanotte Professionals' Hangout 28 01-11-2012 10:25 AM
Thermal break under heated floors/ SOG gitchi gummi Professionals' Hangout 21 02-10-2010 11:12 PM


All times are GMT -6. The time now is 08:24 PM.


Sponsors

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright 2014 John Bridge & Associates, LLC